Number of exits in school ( Educational) building

The minimum required number of exits in a building shall  be  determined  based  on  occupant  load  and width required per person as  appropriate  to  the  type  of  exit  for  respective occupancies, subject to complying with maximum travel distance requirement .


As par National Building code (NBC) 2016 PART- 4 TABLE 5 : 


In Educational occupancy Group (Group B) Maximum Travel Distance is 30.00 Meter in Type 1 and 2 construction and 22.50 Meter in Type 3 and 4 construction type. 
For fully sprinklered building, the travel distance may be increased by 50 percent of the values specified. that is 45.00 Meter in Type 1 and 2 construction and 33.75 Meter in Type 3 and 4 construction type. 
Ramp shall not be counted as an exit in case of basements below the first basement in car parking.

Arrangement of exits

a) Exits shall be so located that the travel distance on the floor shall not exceed the distance given above 
b) Travel distance shall be measured from the most  remote  point within  a  storey  or  a mezzanine floor along the natural and unobstructed path of horizontal or vertical egress travel to the door to an exit.
c) The dead end corridor length in exit access shall  not  exceed  6  m  for  educational occupancies. (see figure below)
[Image: attachment.php?aid=341]
d) Exits shall be placed as remote from each other as possible and shall be arranged to provide direct access in separate directions from any point in the area served


Attached Files Thumbnail(s)
   

Manish Jain Luhadia 
B.Arch (hons.), M.Plan
Email: manish@frontdesk.co.in
Tel: +91 141 6693948
Reply


Messages In This Thread
Circulation Standards for Primary Schools - by sumit patni - 02-03-2015, 10:58 AM
RE: Circulation Standards for Primary Schools - by prakash nair - 08-08-2018, 08:05 AM
RE: Circulation Standards for Primary Schools - by Madhav Joshi - 08-15-2018, 11:51 AM
RE: Circulation Standards for Primary Schools - by Manish Jain - 09-05-2018, 09:45 AM
RE: Circulation Standards for Primary Schools - by dipak.jain - 10-30-2018, 03:34 PM

Forum Jump:


Users browsing this thread: 2 Guest(s)